I have not kept up with the industry, and would like to put a cut off for my panels right before the controller.
I will have 1,000 w on the roof going to a tracer charge controller. I am clumsy enough so I don’t want to take a chance on short circuiting every thing. Most shut off switches seem to be set up for the positive side of a battery. Large connections on a 10 gauge wire. With solar you are supposed to open the ground first? This has given me a headache ?
Compared to parenting, Cat herding is less complicated
•
Posts: 4,198
Threads: 61
Thanks Received: 2,052 in 1,558 posts
Thanks Given: 2,849
Joined: Sep 2017
Reputation:
31
I have pulled the array positive wire from the controller after dark ( basically a spst switch )
for many years with no noticeable ill affect.
Ditto on not hearing anything about the negative let alone the sequence.
And I have heard the cover panels or wait till controller is shut down after dark and do that.
Just don't disconnect the battery first skuh kuh kuh kuh kuh
stay tuned
•
Posts: 528
Threads: 17
Thanks Received: 474 in 293 posts
Thanks Given: 74
Joined: Mar 2018
Reputation:
10
I generally suggest a surface mount circuit breaker on the positive line right before the controller in my builds. Normally for 10 gauge I go for 30-40 amp depending on the output of the combined panel imp. Four $50 250 watt panels from Santan wired in parallel could possibly exceed 30 amps so I suggest 40a.
Actually unless there was shading issue I would suggest running the panels 2 sets of 2 to drop the current. Only Jbox brand is producing 50 amp branch connectors. Unfortunately since the T Tocas brand was bought out, their circuit breakers voltage ratings were dropped from 72 volts back down to the standard 48 volts. Now the only higher voltage options is Midnite breakers in a baby box.
•
Posts: 1,157
Threads: 29
Thanks Received: 641 in 437 posts
Thanks Given: 109
Joined: Feb 2018
Reputation:
4
09-18-2021, 08:33 PM
(This post was last modified: 09-18-2021, 08:39 PM by tx2sturgis.)
This might work, it's rated at 64 amps (2*32 amps)...
https://www.aimscorp.net/aims-power-sola...witch.html
It's designed to suppress the arc that can occur under full solar output conditions and high power levels.
I would assume that some kind of insulator is moved into position as the contacts are drawn apart. But that's just a guess.
_______________________
Wondering about wandering
•
Posts: 1,994
Threads: 64
Thanks Received: 1,368 in 909 posts
Thanks Given: 473
Joined: Sep 2017
Reputation:
14
09-19-2021, 12:10 PM
(This post was last modified: 09-19-2021, 12:31 PM by GotSmart.)
After looking at the current solutions, I have decided to go old school. A couple of house light switches plainly marked. That will clear up any confusion about the power in lines. I would much rather spend about $10 than $150.
The 40 amp details
Compared to parenting, Cat herding is less complicated
•
Posts: 4,198
Threads: 61
Thanks Received: 2,052 in 1,558 posts
Thanks Given: 2,849
Joined: Sep 2017
Reputation:
31
Close enough for a barn......
stay tuned
•
Posts: 1,994
Threads: 64
Thanks Received: 1,368 in 909 posts
Thanks Given: 473
Joined: Sep 2017
Reputation:
14
(09-18-2021, 03:36 PM)justjim Wrote: I generally suggest a surface mount circuit breaker on the positive line right before the controller in my builds. Normally for 10 gauge I go for 30-40 amp depending on the output of the combined panel imp. Four $50 250 watt panels from Santan wired in parallel could possibly exceed 30 amps so I suggest 40a.
Actually unless there was shading issue I would suggest running the panels 2 sets of 2 to drop the current. Only Jbox brand is producing 50 amp branch connectors. Unfortunately since the T Tocas brand was bought out, their circuit breakers voltage ratings were dropped from 72 volts back down to the standard 48 volts. Now the only higher voltage options is Midnite breakers in a baby box.
There is the 1,000 w and unknown volts in that wire. 40 amp rating is easy. Do I need to worry about voltage?
Compared to parenting, Cat herding is less complicated
•
Posts: 528
Threads: 17
Thanks Received: 474 in 293 posts
Thanks Given: 74
Joined: Mar 2018
Reputation:
10
09-19-2021, 07:59 PM
(This post was last modified: 09-19-2021, 08:02 PM by justjim.)
Open circuit voltage on each of those 250w panels is 37.6v and working is only 30.3v. I would not run all four in series but 2 and 2 would be fine.
All four in parallel is 33 amps and 30.3 volts.
2 and 2 is 17 amps and 61 volts
All four in series is 8.27 amps at 122 volts. Unfortunately the Voc at this point exceeds the controller without even considering cold temps or cloud effects that can push it even higher.
•
Posts: 1,994
Threads: 64
Thanks Received: 1,368 in 909 posts
Thanks Given: 473
Joined: Sep 2017
Reputation:
14
(09-19-2021, 07:59 PM)justjim Wrote: Open circuit voltage on each of those 250w panels is 37.6v and working is only 30.3v. I would not run all four in series but 2 and 2 would be fine.
All four in parallel is 33 amps and 30.3 volts.
2 and 2 is 17 amps and 61 volts
All four in series is 8.27 amps at 122 volts. Unfortunately the Voc at this point exceeds the controller without even considering cold temps or cloud effects that can push it even higher.
I had planned for everything being parallel.
On Amazon they have a WOHHOM brand WA40A breaker. One on each line in to give extra safety. $14 each. They are rated for 12 volts.
I do have one of the battery type switches available.
Compared to parenting, Cat herding is less complicated
•