Solar virgin here needing help please.
Just received my Renogy 200w starter system with Rover 20w mppt controller. I have a 100ah 12v agm battery. According to the instructions fuses are required between the panels/controller and controller/battery.
Panel to controller cables are 10awg as are the tray cables. The NEC chart lists max current at 40a for the wire. Instructions say 20a fuse for controller to battery and for panel to controller either a 9a fuse for series or 18a for parallel. Is that for how the panels are wired? I'm confused. If it is the panels I think they are parallel.
Also what size fuse from battery to fuse block if needed. Power use will be limited to a 15qt truck fridge, cpap, and charge ports for flip phone and Kindle.
Do you prefer fuses to breakers and what style do you recommend?
Thanks in advance.
Just received my Renogy 200w starter system with Rover 20w mppt controller. I have a 100ah 12v agm battery. According to the instructions fuses are required between the panels/controller and controller/battery.
Panel to controller cables are 10awg as are the tray cables. The NEC chart lists max current at 40a for the wire. Instructions say 20a fuse for controller to battery and for panel to controller either a 9a fuse for series or 18a for parallel. Is that for how the panels are wired? I'm confused. If it is the panels I think they are parallel.